  1. 16 minutes ago, W7BE_Bob said:

    ... Yes, 4 ga is rated for 70A but I'm not concerned.

    4ga should be good up to 160a if not bundled or in conduit. 
    90a circuit breaker will protect it just fine  

    Cheers

    Walter

  2. 1 hour ago, Jim McGarvie said:

    OK, I'm with you. I've got a 60A controller and using 4 ga. wire between it and the inverter. I found this page and think a 70A or 80A breaker should do. https://www.amazon.com/amp-Circuit-Breaker-12V-Motorhome/dp/B07SHRCSTJ?th=1.

    Thanks Walter.

     

    I was a little uncomfortable taking a chance on a no-name Chinese safety device... so I used this one:

    Bussmann CB285-90 Surface-Mount... https://www.amazon.com/dp/B01FWMLZD6?ref=ppx_pop_mob_ap_share

    cheers

    Walter

  3. 1 hour ago, Jim McGarvie said:

    Does the big fuse between the inverter/charger and batteries serve the purpose or do I need something between the controller and the inverter/charger in addition?

    The big fuse between the inverter and the batteries protects the WIRE between the battery and the inverter. That’s why it’s close to the battery and it is sized according to the max current of that wire gauge (and some other factors).  
    Another circuit breaker or fuse needs to be between the inverter and the solar controller. It needs to be on the inverter end of that wire and sized no bigger  than the max current of that gauge of wire. So the fuse or circuit breaker should be rated at least as much as your controller can produce, and at most the max current that the wire is rated to carry. 
    Cheers,

    Walter

  4. 58 minutes ago, Jim McGarvie said:

    2. ...Is there any reason to add a second switch between the controller and the batteries (in my case, the inverter/charger)?

    Thanks For any suggestions.

    Jim

    Yes, this needs a disconnect, but more importantly the wire needs overcurrent protection. A high-capacity DC circuit breaker on the inverter end of the cable serves both purposes. 
    Cheers

    Walter

  5. Thanks!

    Another update on the acoustic foam. I ordered some 3" thick foam and cut 2 blocks about 6"x3"x1-1/2" and tucked them up on the sides of the duct, directly beneath the evaporator intake. This blocks the path straight down from the evaporator.

    Subjectively, they cut down quite a bit on the perceived fan noise. The higher-pitched blower whine is gone. Mostly what I hear now is a lower-pitched rushing of air and a little hum from the compressor.

    My unscientific iPhone dB measurements read 2-3 dB difference with and without the foam blocks, with some visible reduction in volume between about 1000 and 5000 hz.

    According to the dB meter, the new front unit still isn't any quieter than the old middle unit. But subjectively, I'd say its a big improvement.

    Cheers,

    Walter

    foam blocks.jpg

    • Thanks 1
  6. 4 hours ago, michaelivan said:

    Thanks for the help.  Mine is neo-angle and I have a couple of options.  I have found outer skylights from Ikon and Specialty Recreation.  Both look like they will fit.

    I'd imagine yours is similar to mine except for the shape. There's nothing about mine that makes it inherently a '2-layer skylight'; it's just a regular outer bubble and a slightly lower inner bubble. Screws go down through both to secure them to the roof. Apparently the outer bubble does a pretty good job of stopping the UV; as far as I know mine were original from 2003 and the inner bubble didn't show any sun damage. The outer bubble was hazed all over and cracking.

    Couple-years ago when I needed to order a replacement, I had a hard time determining whether the new bubble was a '2-layer' bubble and would have room for the inner bubble. So I measured as best I could and hoped for the best. Ikon's smoked skylight turned out to be almost identical to my old outer bubble.

    Cheers,

    Walter

  7. 4 hours ago, michaelivan said:

    Swapped out the sensors and nothing changed.  

    One last easy thing to try... swap circuit boards between two units? 
    If that’s the problem I can supply another good board. 
    I just replaced a rooftop unit. Its not as glamorous as it sounds.
    It’s a lot of trouble and expense, and then you wind up with a shiny new AC that performs just a little bit better than the old one.  
    Cheers

    Walter

    4 hours ago, Dr4Film said:

    Seems to me that one other member did the same switch and the plug and play was fine EXCEPT for securing the AC to the ceiling bracket. I believe the bolt pattern is not the same.

    Yeah, that was my take-away from his story. I think that was buried in the thread about Penguin II availability?

    The only experience I have is replacing a ducted Penguin with a Penguin II. In this case, there are metal tabs welded in the corners of the roof opening for the bolts to pass through. And the bolts pass up pretty close beside the ceiling duct. So there's not much room for the bolt spacing to change before you're cutting up the ductwork. 

    I remember seeing some specs on other units that showed the bolt spacing to be a lot more narrow. If you've got a non-ducted setup with the air distribution box on the ceiling, maybe its a lot more forgiving. But if you have a central duct up in the ceiling, that might make the replacement a lot less clean.

     

    Cheers,

    Walter

    bolt hole.jpg

    • Like 1
  8. Hi everybody. Just a followup to this post.

    The new unit has been installed and running for a couple weeks now. Just a few cosmetic details to complete, like making a plug to fill a big hole where I moved the kitchen fan thermostat over to make room for the CCC2.

    Installation was pretty straightforward, but here are some notes on my experience.

    Removal: The old square gasket gets fused to the roof like you wouldn't believe. I mean like 3M 5200 fused to a boat deck. If I were doing it again I'd cut some wedges out of 2x4 scrap to keep upward pressure on the seal, then get in there with a long knife and water lubricant to cut through the middle of the gasket rather than try and get a putty knife under the gasket. Once the unit has been lifted off, it's pretty straightforward to scrape the gasket off with a sharp putty knife and then clean up with solvent. 

    Duct was deformed: The old unit had apparently been retightened over the years, to the point where the drain cups were touching the roof. This caused the ceiling duct to be forced down >1/2". It didn't rebound on its own, so I cut a wood spacer to go between the roof structure and the rear of the transition stub, and screwed the sheetmetal transition duct back into the wood to hold it up and level. In its final position, the AC's bottom pan is less than 1/4" above the duct extension, so there's not much room to further tighten the bolts. Not without shortening the transition duct.

    Bolt tightness: The regular instructions say to tighten bolts to 40-50 in-lb.  I didn't get the bolts anywhere near that tight before the two stacked gaskets had compressed 1/2". So I stopped there. I also ignored the drain pan instructions where they say to put a double-stacked strips of gasket at the back of the unit (which would hold the unit up off the normal 3/4" hard-foam pads and support the back of the pan). So I doubled up the hard-foam pads at the back to make them 1-1/2" thick and tightened the bolts till the 2" thick stacked square gaskets had compressed to 1-1/2". This left the bolts way looser than 40 in-lb. But if I go anywhere near that toque spec it'll pull the unit right down on the deck. I think I'll make some marks on the roof with sharpie so I can tell if is the units moves at all in transit and go from there.

    Electrical: New units come with a mobile-home electrical connector pre-installed on the power cable. At least mine did... but Dometic only gave me 1 half of the connector pair. The connector is thin/flat and certified as a junction box. This opens up some additional room for airflow around the side of the duct (vs- the old steel junction box), so I bought the other half of the connector pair and used it. There are many variations of this Self-Contained Power Connector (SCPC), and here is the specific part if you need the other half for 12ga romex:

    https://www.mouser.com/ProductDetail/molex/19045-1000/?qs=c7V%2bsbZfmqvqLYL%2bCrIKLw%3D%3D&countrycode=US&currencycode=USD

    Noise: I was really hoping to wind up with a quieter unit. It is not, unfortunately 😒. In fact my iphone dB meter says it's about 2dB louder than my old center unit. Almost all of the noise is from the fan though. Pretty much can't hear the compressor at all. So, I'm going to experiment with some blocks of acoustic foam on the duct sides directly beneath the evaporator intake and see if I can trap some of the fan noise rather than let it come straight down through the filter. Initial experiments with wadded up kitchen towels were encouraging.

    Cheers,

    Walter

     

    • Like 1
  9. 13 hours ago, michaelivan said:

    I am having issues with one of my original Dometic Penguin heat pumps on my 2003 Monaco....It is starting to misbehave in the following manner:  The unit will come on, start to cool with the air reaching about the 57-58 degree range as measured at the ceiling vent.  After about 5 minutes, the compressor kicks off, the fan kicks into high speed and runs for about 2-3 minutes.  The unit then shuts off.  

    Can you see up into the evaporator? That sounds to me like what the AC would do if the evaporator was frozen up.

    If it’s not freezing up, maybe something wrong with the freeze sensor? In that case maybe swap the freeze sensor with one of the other units. 
    Cheers

    Walter

  10. 1 hour ago, granvillebarker said:

    Walter,   
     

    What a great idea, that sounds easy and should work!  
     

    I could get three of the new penguin-2 boards and an easy-touch. 
     

    Granville Barker

    Yep. But you’d also need to add a remote temp sensor for the 3rd unit. If I understand it correctly, Temp on the thermostat is only for Zone1 and all other zones need their own sensor connected to the rooftop unit.  
    Cheers,

    Walter

  11. 1 hour ago, rpasetto said:

    @Walter

    I see how similar they are now looking at the wiring diagrams.  Not quite though.  Looks like some terminal designations changed....  if I understand what the schematics show:   

     - But on the old board, T2 is wired to the control the reversing valve with other connection of valve going to the C terminal on the run cap.  On the new board, either T4 or T7 serves as control for the reversing valve and the other (internally connected to T6?)  gets to the to 'C' on the run cap.   Not sure of best way to deal with this, maybe testing with a meter should show which is which.

    The new ccc2 control boards are going for low 100's and up, but there may be a few available which were pulled when new Penguin units were converted to use the old CCC thermostats.  I'll check eBay once in a while.

     

    PS:  I'm not in TX now but when I'm there you're probably 1.5hrs away.... or 'just down the road' in TX distances.   I'll be back in the fall so if you decide to do this project & the timing is right I could come help.

    T6 and T7 are boxed off on the board and labeled a neutral, so I’m feeling pretty sure they’re just two COM terminals and there’s nothing fancy happening with the reversing valve. As far as I can tell, reversing valves are very standard and are either energized in cool or energized in heat. 
    I’ll watch eBay and see if one comes along. 
    Stop by when you’re by the hill country!  We’re right by Garner state park. 
    Cheers

    Walter

  12. 2 hours ago, Dr4Film said:

    Walter, that "new" sensor noted in your diagram is not really new as there is an ambient temp sensor (P3) in the old diagram also but never used. The early versions of the CCC-2 Thermostat had 12 buttons one of which was Outside Temp but it is no longer used by the 10 Button CCC-2 thermostats sold today. Everything else is the same.

    Ok. Yep, I found it. On the new unit the outside sensor is out on the side of the pan, on the old unit it's screwed to the inside of the circuit board housing. 

    The other apparent differences are:

    • Reversing valve neutral is connected to circuit board COM instead of spliced into the dual-capacitor COM. 
    • Old unit only uses fan Lo and Hi, Med is not used and has a splice cap on it.

    So far the major pieces all look identical. The new circuit board looks to be the same size too, so I think it'll pop right onto the old standoffs and be a drop-in replacement. I'd need to verify a few things like 1) that the reversing valve is still energized for heat, 2) similar specs on the thermistors.

    I might just go ahead and be the guinea pig.

    Does anybody have a CCC2 circuit board they'll let go for cheep?

    Cheers,

    Walter

     

  13. 1 hour ago, rpasetto said:

    For the old-to-new board swap, a different and admittedly easier task.  While a good meter to check voltage levels may do it,  a scope may be necessary if pulse width is involved int the signals.  What do you think the thermistors are for?  Overtemp?  

    Anyway the new control board runs over a hundred bucks; not cheap but it sure beats shelling out for a new AC.    The open question is: who tries it first?  I vote for you since you already have a lot of info and likely the know how to do it.  🙂

    @William  here's new control board... may be less elsewhere:

      https://pantherrvproducts.com/dometic-3312022-000-replacement-ccc2-electronic-control-board-3312227-000/

    Pulse widths? I'm not sure there's anything nearly that sophisticated going on here. The compressor is on or off. The fan is standard 3-speed AC motor. The reversing valve is on or off. Amp draws of each component have got to be pretty similar to the old components. 

    Take a look at the two attached wiring diagrams. Pretty dang similar, right??? Except for the new Outdoor Temp Sensor P3 (which appears to be screwed to the edge of the base pan). I think that's the only new component (edit- nope, I just noticed 'ambient sensor' on the old diagram).

    Hopefully the reversing valve is the same normally-on or normally-off design as the old penguin. In the new design, the reversing valve has two connections to the circuit board, in the old design it has one connection to the board, and the other to neutral.

    I'm sure Dometic wouldn't encourage anyone to do this rather than buy a new unit, but as far as I can tell, the new penguin is just another very low-tech window-unit heat pump that's been reconfigured to fit inside the rooftop shell.

    If anybody has access to a junk'd penguin II and can give me a board and thermistors, I'll try it!

    Cheers,

    Walter

    Old_penguin.jpg

    New_penguin.jpg

  14. 1 hour ago, directorsusa said:

    I have been following this and I was hoping to see someone identify maybe where the connection is for the alternator to the house batteries. That way I can just remove this connection or maybe fuse. I have not seen this mentioned yet? 

     

    As a side note I have obtained new lifepo4 batteries straight from China and using third-party BMS. Much cheaper than battleborn and much more capacity. I got 8 3.2v 280Ah batteries shipped for around $1k. Bms about $100. So 7,100 watts for around $1100 compared to $1000 for 1200 watts from battleborn. Only way to go if you're going to need new batteries soon. 

    And please keep us posted! I am keenly interested to see how this works out for you. 
    Thanks

    Walter

  15. 2 hours ago, rpasetto said:

    #Walter,  ... To adapt the new CCC2 type board to the older AC requires knowing details about the internal electronics of the units and the control signals, or  trial-and-error with a lot of luck.  I have neither.  

     

    I learned a lot here.

    I certainly agree on reverse engineering the communication protocols, but swapping the board is different. I’m not sure it would involve any of that!

    The old control board has some logic on it and then it engages some relays to actuate one compressor, one fan and a standard reversing valve  The new board has exactly the same OUTPUTS to one compressor, one fan and a similar reversing valve. 

    I’d bet money it’d transplant real easy. The control board doesn’t know what it’s relays are connected to and would be happy turning on lightbulbs instead of compressor and fan . The new unit looks like it has two thermistors that the old unit didn’t have, so those parts would be required .

    Years ago I put a 3rd party control box and thermostat on a boat heat pump. The control board don’t care what brand of compressor  it’s hooked up to.
    I can’t think of any reason the penguin II control board would care if it’s hooked up to an old compressor, or transplanted into a window unit for that matter, as long as the components are similar.

    Cheers

    Walter

     

  16. 7 hours ago, Dr4Film said:

    I always use Northwest RV Supply for all of my switch needs as they seem to have the best selection and variety too.

    Here is their web site address for Switches - http://www.nwrvsupply.com/category/176.html

    Here is their web site address for the momentary switch you are inquiring about - http://www.nwrvsupply.com/176/12675.html

    They also carry the RED indicator light that is usually adjacent to the Water Pump switch. Those never lasted very long as they have an incandescent bulb inside. I have since switched those out and now have small LED's in the same place. I had purchased those from the RV shop in Wildwood FL which has changed ownership and is now Lazy Days RV. Not sure if they still carry them or not.

    Photos of before & after change-out.

    Tank Level Indicator Panel-03.jpg

    Water Pump LED-01.JPG

    I like that indicator light. Is that a panel-mount LED that you installed in a switch blank, or was it supplied that way with terminals on the back like a switch?

    Thanks,

    Walter

  17. 7 hours ago, rpasetto said:

    Here's a page from the 07 Sig WD book which pretty much confirms what you said.  The diagram doesn't appear in you WD book or mine but I doubt too much has changed.  Note the "Bathroom Dometic controller" (in the Penguin II) connects second in the Daisy chain from the Bedroom AC.   Too bad that " EasyTouchRV" thermostat wont work with holder Dometics.  Wondering if any of the "smart" thermostats for houses could be adapted to work with both.  

     

    Yeah, I'm sure it would be a ton of work and recabling to try and adapt a residential thermostat. I don't think the CCC is a thermostat in the conventional sense anyway. It seems more like a remote display for the rooftop unit's circuit board.

    If you're wanting to adapt something... I think the easiest approach would be to transplant a Penguin II circuit board into the older unit.  At the end of the day, they are both just straightforward heat pumps, right? Both have one compressor, one fan and a reversing valve. Maybe need to also transplant some additional small parts like evap temperature probe.  

    Cheers,

    Walter

  18. 25 minutes ago, rpasetto said:

    The reason I asked is I am not sure how the aquahot control will work. Currently the only communication from thermostats is first to the AC unit and, presumably then to the Aquahot.  So the front Therm. controls the front AC via its RJ12 "telephone" cable and somehow gets the signal to the Aquahot for its front zone.  But how the rear thermostat gets its signal to the Aquahot for zones in rear is unclear to me.  Does the cable from the Therm "daisy chain" to rear AC, then to mid AC and then to Aquahot?  Or other possibilities: Therm  -> RearAC -> MidAC -> Aqhot   ... or Therm-> RearAC-> Aqhot-> MidAC ...?  I looked in my wiring diagram book and could not find that info; depending on how control cables are connected seems relevant.

    The aquahot is actually controlled by the rooftop units. I think the CCC is more of a remote display and temperature sensor than it is a conventional thermostat. 

    In my setup, each of the three aquahot zones is connected to its respective rooftop unit. So when a rooftop unit's control board calls for Furnace, it actuates one of the aquahot zones. It doesn't matter how the CCCs are connected to the rooftop units, they will still control the aquahot in the same manner.

    Does that make sense? Check out the attached diagram from the Penguin installation manual. This shows the "4 conductor communication cable" (phone cable) from the CCC to the front unit, and then daisy-chained to the back unit. In our case the two furnaces are really two zones on the aquahot, and they are each connected to a rooftop unit, not the CCC. Since my middle unit is already Zone2 on the old CCC, it's got an 'internal temperature sensor' and is ready to be Zone2 on the new CCC2.

    So the only change needed to run the middle Penguin II from the forward CCC2 is a 4 conductor communication cable from my front unit to my middle unit. All of the other wiring will be the same.

    Dometic_Wiring.jpg

  19. 3 hours ago, granvillebarker said:

    So your saying the CCC2 will run older units that the 5 button units controlled?

     

    I was looking at the EasyTouchRV, and it says its compatible with the CCC2 units.   Has anyone tried one:

     

    https://www.microair.net/products/easytouch-rv-thermostat?variant=32199143555156

     

     

    --

    Granville Barker

     

     

    No, I am not suggesting that CCC2 will run older units. 

    I'm saying that when I replace my middle unit, my plan is to connect that new Penguin II to the new CCC2 that now controls my forward Penguin II.

    The easytouch sure sounds nice. https://www.youtube.com/watch?v=YYXV927O6_M

    Remote control by wifi would certainly be a nice perk. And it's not a whopping 6" wide. 

    I had to move my kitchen fan thermostat over to make room for the CCC2, which leaves a big hole I still need to fashion a plug for. 

    Cheers,

    Walter

  20. 53 minutes ago, rpasetto said:

    I think most if not all 42' and larger coaches were set up the way yours is, with the rear Thermostat controlling the mid unit (near-front).  You raise an interesting point about changing cabling from the CCC2 to run a new mid unit from the front.  Let us know how it works out when you do it..

    Hopefully it'll be a while! (unless I can find somebody to buy my old working units...)

    I'm pretty confidant that hanging a new Penguin II on the forward CCC2 would strictly be a matter of running one phone cable from the front unit to the mid unit! This would allow replacing just the middle unit with no need for the CCC compatibility board. 

    Cheers,

    Walter

×
×